  • in reply to: Instantaneous bather load reduction for low turnover rate #38116
    Neil Ballard
    Participant

    Great, thanks for that.
    I did the calculation another way (reducing the Max Bather Load by the same percentage as my actual flow rate was slower than that calculated by the (Maximum Bathing load x 1.7)formula above) and came to that conclusion as the two results were similar but I’m happy you’ve confirmed it for me.
    They really ought to extend that division bar over the x 1.7 in their text to make it clear!

    in reply to: Instantaneous bather load reduction for low turnover rate #38105
    Neil Ballard
    Participant

    Thanks for your reply but no it doesn’t answer my question. I need to calculate the reduced Instantaneous Bather load as per the PWTAG Code of practice page 18 because our circulation rate is lower than recommended. On that page they print the calculation but it is not very clearly laid out and it is hard to tell whether you multiply or divide by the factor of 1.7. That is my question.